A commercial building has a 400amp single phase main panel. Another electrician installed a 200amp single phase "sub" panel from this main panel.
The 400amp main panel had no available spaces for the 200amp breaker, so he tapped the two hot conductors on the line side of the 400amp breaker in the factory supplied terminals. (this panel had two extra taps) The neutral conductor was tapped on the neutral bar of the main and the ground conductor was tapped on the ground bar of the main panel.
The two hot conductors are upstream from the 400amp breaker and technically speaking they are not drawn from the main.
The neutral and the ground are on the main.
Is this 200amp panel a sub-panel or a second main panel?
The other electrician said it was a second main, therefore on the 200amp panel, the neurtrals must be bonded to the grounds as opposed to isolated.
The other electrician did a load calculation and all is well within limits.
What is your determination of this and what does code say about this?
The 400amp main panel had no available spaces for the 200amp breaker, so he tapped the two hot conductors on the line side of the 400amp breaker in the factory supplied terminals. (this panel had two extra taps) The neutral conductor was tapped on the neutral bar of the main and the ground conductor was tapped on the ground bar of the main panel.
The two hot conductors are upstream from the 400amp breaker and technically speaking they are not drawn from the main.
The neutral and the ground are on the main.
Is this 200amp panel a sub-panel or a second main panel?
The other electrician said it was a second main, therefore on the 200amp panel, the neurtrals must be bonded to the grounds as opposed to isolated.
The other electrician did a load calculation and all is well within limits.
What is your determination of this and what does code say about this?