P patsy Member Location new jersey Oct 19, 2009 #1 i know the table for main panel ampacity what is the sub panel ampacity r they 310.15 for mains and 310.16 bfor sub
i know the table for main panel ampacity what is the sub panel ampacity r they 310.15 for mains and 310.16 bfor sub
V Volta Senior Member Location Columbus, Ohio Oct 19, 2009 #2 It is all T310.16 (for those types of wires), with an exception of 310.15(B)(6) only for "main power feders", or service-entrance or -lateral conductors, as 120/240 single-phase for dwelling units. Otherwise, stick with Table 310.16.
It is all T310.16 (for those types of wires), with an exception of 310.15(B)(6) only for "main power feders", or service-entrance or -lateral conductors, as 120/240 single-phase for dwelling units. Otherwise, stick with Table 310.16.
P patsy Member Location new jersey Oct 19, 2009 #3 its a commercial building so i can use for both main panels and subs the one table/
V Volta Senior Member Location Columbus, Ohio Oct 19, 2009 #4 Yup. 310.16 is our friend! (With 110.14(C), of course.)