nerspellsner
Member
I have installed a 400 amp fused disconnect used as the main service disconnect for a single family dwelling. Two ground rods are connected to it at this point. It is feeding a 400 amp automatic transfer switch which then feeds two 200 amp main breaker panels. The grounds and neutrals are seperated in both panels. A seperate ground kit and a seperate isolated neutral kit were included with the 400 amp fused disconnect. The neutral kit included a green bonding screw. Now here comes some bonding questions about this installation. Would this screw be considered the main bonding jumper? Is the screw all that is needed for the connection between the ground and neural? If it is, how can this screw equal the same as a conductor sized for the main bonding jumper? Would installing a conductor between the ground and neutral along with the screw be acceptable or does this create a parallel path? Is a main bonding jumper and a main bonding conductor the exact same thing? Thanks.