highendtron
Does anyone know where the code refernece is requiring a disconnect when the service entrance cable is further than 10 foot from the metercan to the panel? Thanks.
The distance may be a local requirement but it is not an NEC requirement.Does anyone know where the code refernece is requiring a disconnect when the service entrance cable is further than 10 foot from the metercan to the panel? Thanks.
I see 230.91
Remember, you can also place the main disco inside, back-to-back with the meter, and still have the panel elsewhere.Around here 10' into the building and you'll get a red violation sticker which means you'll either move the panel closer or put the OCPD adjacent to the meter.
We have 16feet per ahj
That is quite generous. In my area there is no "official" length that service conductors can run in side a building.
Chris