dicklaxt
Guest
Thanks Jeff exactly the way I drew it from your circuit description.
Heres the scenarios as I see them
Ckt "A" with transfer selected,tie open,then Ckt "A" is feeding "A" bus and CKT "B" feeding "B" bus everything okay so far,now close the "Tie" and "A" and "B" are butting heads(thats not good) so there is probably an interlock to stop the tie from being closed,now open "B" main and Ckt "A" is feeding both bus "A" and "B",things are okay again.
Now transfer switch selects Ckt "B",Ckt "B" is feeding both bus "A" and "B" whether tie is open or closed(not the norm I would say) so again there must be an interlock to keep the tie from being closed when both mains are closed.I now see Ckt "B" feeding bus "A" thru the transfer switch and bus "B" is dead because of the interlock having main "B" open.
It appears to me that the transfer switch is only intended to be there so that bus "A" is the critical bus and can be fed from either Ckt "A" or "B" and bus "B" would be offline because of the interlock that locks out "B" main.
So assuming all that to be true then the main-tie-main interlock must have a hitch in its get a long where Ckt "A" or Ckt "B" can close in on each other before the tie opens
which is what others have said, phases being out of sync,I think..
I normally think of a transfer switch being used between normal feed and a generator feed on an Essential bus without a tie. Is this setup referenced here a norm in the industry?I guess a main-tie-main electrically operated in a control scheme is in itsself a transfer switch.
dick
Heres the scenarios as I see them
Ckt "A" with transfer selected,tie open,then Ckt "A" is feeding "A" bus and CKT "B" feeding "B" bus everything okay so far,now close the "Tie" and "A" and "B" are butting heads(thats not good) so there is probably an interlock to stop the tie from being closed,now open "B" main and Ckt "A" is feeding both bus "A" and "B",things are okay again.
Now transfer switch selects Ckt "B",Ckt "B" is feeding both bus "A" and "B" whether tie is open or closed(not the norm I would say) so again there must be an interlock to keep the tie from being closed when both mains are closed.I now see Ckt "B" feeding bus "A" thru the transfer switch and bus "B" is dead because of the interlock having main "B" open.
It appears to me that the transfer switch is only intended to be there so that bus "A" is the critical bus and can be fed from either Ckt "A" or "B" and bus "B" would be offline because of the interlock that locks out "B" main.
So assuming all that to be true then the main-tie-main interlock must have a hitch in its get a long where Ckt "A" or Ckt "B" can close in on each other before the tie opens
which is what others have said, phases being out of sync,I think..
I normally think of a transfer switch being used between normal feed and a generator feed on an Essential bus without a tie. Is this setup referenced here a norm in the industry?I guess a main-tie-main electrically operated in a control scheme is in itsself a transfer switch.
dick