- Wisconsin
- PE (Retired) - Power Systems
Let me try to explain this better. Power comes out of a 400a breaker at a outdoor sub. 13.8kv underground to a existing building entering a load interupter switch[ a main without a key] ,busses to a fused interupter switch witch feeds into the building sub. , outdoors after the fused switch there is a switch [tie without the key] than another fused switch going in the building to another sub. than after that switch there is aload interupter switch [main without a key] than out to the next building underground. Picture this with 3 buildings. As long a 1 switch is open somewhere in this senerieo all is good. You would have 2 breakers feeding 2 systems. If that switch gets closed you would complete a circle and that would not be good. There must be a violation here somewhere. You would also be feeding some of these load interupter switches on the load side so if you open the switch to open the door it would still be hot on the load side. This system is serviced by only experienced people.
It now sounds like you describing a loop feed arrangement and not a parallel one. How many sources (substation transformers or utility feeds) are there?
It is common to have one source feed (2) breakers, one feeding the loop clockwise, the other counter clockwise. In these cases the fault current,on the switchgear bus, is not doubled like it is with a parallel feed.