Main Water Line Grounding

Merry Christmas

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Do I need to ground the main water line if there is a UFER ground already in place? I am in California
IMHO... You are not grounding the main water line. Its already grounded. :) But, you would be required to bond the main water line if the main water line is comprised of a conductive material and if it is accessible after installation. 250.50
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If a metal buried water pipe qualifies as an electrode then it must be used as part of the grounding electrode system (GES). It is not optional even with a CEE.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
1724713942324.png

Note that this more or less says all that are present must be used, and the water pipe electrode is one of the (A)(1) through (A)(7)

Also as mentioned if you have metallic water piping system but not a water pipe electrode, you still need to bond the water piping system per 250.104(A).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Also as mentioned if you have metallic water piping system but not a water pipe electrode, you still need to bond the water piping system per 250.104(A)
That's correct, and note kwired's the use of the word system. It the water piping system is not all metallic it does not require bonding.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
That's correct, and note kwired's the use of the word system. It the water piping system is not all metallic it does not require bonding.
Though there has been some debate on here before on how much of the system needs to be metallic to be called a metallic system.

Over time you may have a system that once was all metallic but has had significant amount of modifications with non metallic piping.
 