- Wisconsin
- PE (Retired) - Power Systems
No arguments here with anything posted in response to my described approach.
... except I disagree that gf settings will affect arc flash PPE requirements. Granted they could minimize the incident energy for an Arc Flash, and minimize damage as well.
I suppose I'm driven by reliability and uptime, while still meeting code requirements. That's an easy philosophy to defend to a Data Center manager.
However, I do see merit to a lesser GF adjustment in some cases, so I appreciate the alternative point of view, and will consider it where possible.
To Jim D I pose the question: On a 35kV, 600A circuit, where do you set your ground-fault pickup?
John M
Ground fault settings do not directly impact arc flash. My comment was meant to show that I keep my branch circuit devices as low as I can which then allows me to keep my GF settings lower than maximum.
On 35kV, there are too many items to consider to answer such a vague question. A single relay protecting an underground campus network of fusible switches would probably be handled differently than an open air substation containing 5 station breakers.