Maintenance Mode Switch

Status
Not open for further replies.

Curt Fitz

Owner, Triangle Electric, Fayette, MO
Location
Fayette, Missouri
Occupation
Contractor, Master Electrician
We were told that the NEC requires an MMS on all distribution panels. I cannot find the provision, even with the NFPA Link. Help?
 
A distribution panel is not defined in the NEC. But I suspect the MMS is related to arc energy reduction, it’s not an area I am familiar with. I would start by looking in Art 100 definitions and 240 Overcurrent Protection.
 
240.67 (B)(2). It is one option if using fuses rated 1200 A or higher with a clearing time of more than 0.07 seconds.

0.07 seconds is about 4 cycles.

effective date jan 1, 2020.
 
We were told that the NEC requires an MMS on all distribution panels. I cannot find the provision, even with the NFPA Link. Help?
Good question, thanks for asking. When someone tells you that MMS are required on all distribution panels, or similar, ask fora reference. Or ask here, that way we can all learn…
 
Status
Not open for further replies.
Top