goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
Is there anything special I need to know about making up CAT-5 male ends. I don't have the tool yet but I can't imagine that it's that difficult. Is there any reason I need to make up cables other than straight thru as shown on this site : http://www.groundcontrol.com/galileo/ch5-ethernet.htm ?
The job I'm bidding on will be using three of these Antminer S9 bitcoin units initially and possible three more in the future :
https://miningwarehouses.com/bitcoi...MI5bm87Lna1gIVxkSGCh3xvgu4EAAYAiAAEgJ2O_D_BwE
The specs show that they draw 1375 watts each so it seems that I will not be able to run two of these on one 15 or 20 amp circuit. If any of you have any experience with these items would you please post it here ? There is one 20A circuit already available in the location where they will be installed. I'm thinking I can run another 20A MWBC to handle the other two unless there is a problem with these units running with a shared neutral. If the HO's are serious about installing the other three I may install a sub-panel.
Thanks
The job I'm bidding on will be using three of these Antminer S9 bitcoin units initially and possible three more in the future :
https://miningwarehouses.com/bitcoi...MI5bm87Lna1gIVxkSGCh3xvgu4EAAYAiAAEgJ2O_D_BwE
The specs show that they draw 1375 watts each so it seems that I will not be able to run two of these on one 15 or 20 amp circuit. If any of you have any experience with these items would you please post it here ? There is one 20A circuit already available in the location where they will be installed. I'm thinking I can run another 20A MWBC to handle the other two unless there is a problem with these units running with a shared neutral. If the HO's are serious about installing the other three I may install a sub-panel.
Thanks