Manholes (mixed systems) H.V. Phone?
yoopersup
Article 3.14 Manholes. I can find nowhere in the Manhole section that prevents a Manhole from containting 4160-13800 & 100 pr.Phone the H.V.cables are single conductors in pvc passing thru.Phone in the same manholes. The cables and Manholes are the Owners. I think its wrong but where do I find a Article or section that prevents it?? Any Ideas on this? Most places I;ve run into have seperate power and communitions manholes.
Re: Manholes (mixed systems) H.V. Phone?
See 800.11(A)
Roger
That sure looks like it! Funny no reference in the Manhole section to this Section.Since Deregulation Lotta things like this Have been coming up.
"Underground communications wires and cables in a raceway, handhole, or manhole containing electric light, power, Class 1, or non?power-limited fire alarm circuit conductors shall be in a section separated from such conductors by
means of brick, concrete, or tile partitions or by means of a suitable barrier."
I wonder if they consider plastic conduit a sutiable barrier.
Petersonra
In the duct bank Yes, PVC no problem BUT passing thru the manhole ??? Most manholes well be at least 6x8 x 8ft in hight so like a small room . All cables well be racked passing thru,