Recent PSE power outage for 4-5 days in area due to PNW 'bomb cyclone'
Our church food bank has 8 each 600W commercial freezers and refrigerators
Member will donate an 8 kW generator, problem is how to hookup low cost (very limited funds as typical of chruches these days).
My estimate is that the permits (over $200 alone here for even a single outlet) and a subpanel with manual transfer switch would be near $500 with volunteer labor.(all refrigerators and freezers now plug into 20A outlets fed directly off 4 separate 20 A main panel breakers)
Option 1 is obviously to simply run 8 extension cords during any outage to avoid xfer switch and any code issues which would be innconvienient. .
Option 2 is my question as per code:
What if any code section would prohibit a separate box with 4 20 A outlets, 4 ea 3 way light switches used as transfer switches (common to outlet, one traveller to each of existing panel 20A breaker VIA PLUG AND CORD TO EXISTING REFIGERATO UNIT OUTLETS, the other traveller to a single extension cord via separate non NEC (aircraft surplus breaker) to generator. In case of power outage, all needed than is start generator and plug in main split 120/240 extension cord to generator, and flip 4 switches.
Code wise, I do not see any prohibitions against this, with the main extension cord disconnected at each end it is simply a switch box in the refrigeration unit cord.
Our church food bank has 8 each 600W commercial freezers and refrigerators
Member will donate an 8 kW generator, problem is how to hookup low cost (very limited funds as typical of chruches these days).
My estimate is that the permits (over $200 alone here for even a single outlet) and a subpanel with manual transfer switch would be near $500 with volunteer labor.(all refrigerators and freezers now plug into 20A outlets fed directly off 4 separate 20 A main panel breakers)
Option 1 is obviously to simply run 8 extension cords during any outage to avoid xfer switch and any code issues which would be innconvienient. .
Option 2 is my question as per code:
What if any code section would prohibit a separate box with 4 20 A outlets, 4 ea 3 way light switches used as transfer switches (common to outlet, one traveller to each of existing panel 20A breaker VIA PLUG AND CORD TO EXISTING REFIGERATO UNIT OUTLETS, the other traveller to a single extension cord via separate non NEC (aircraft surplus breaker) to generator. In case of power outage, all needed than is start generator and plug in main split 120/240 extension cord to generator, and flip 4 switches.
Code wise, I do not see any prohibitions against this, with the main extension cord disconnected at each end it is simply a switch box in the refrigeration unit cord.