Manual Transfer Switch at mobile home

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Existing 200A meter/service pedistal at mobile home, with 3 breaker slots for branch ckts
Would this work?
Install a 200 A feed thru panel 8/16 ckts
Mount on outside of mobile home
Run feed from existing meter service to this new feed thru panel, and refeed mobile home
Install interlock kit on new 200 A feed thru panel with genny inlet
This minimizes outage and no dealing with poco
Thanks, I have only done 2 mobile home services 40 years ago
 
Existing 200A meter/service pedistal at mobile home, with 3 breaker slots for branch ckts
Would this work?
Install a 200 A feed thru panel 8/16 ckts
Mount on outside of mobile home
Run feed from existing meter service to this new feed thru panel, and refeed mobile home
Install interlock kit on new 200 A feed thru panel with genny inlet
This minimizes outage and no dealing with poco
Thanks, I have only done 2 mobile home services 40 years ago
That would work, no interlock available for the existing service disconnect? Or is it a six switch rule disconnect?
 
Remember the FAS inspection if you mount it on the house.

I'd rather change out the pedestal for a standard main breaker 3r panel and throw the standard meter on an Hframe. They make standard 3r panels with interlocks available.
 
Remember the FAS inspection if you mount it on the house.

I'd rather change out the pedestal for a standard main breaker 3r panel and throw the standard meter on an Hframe. They make standard 3r panels with interlocks available.
Yes that is an option for 3R panel and I wasn’t sure if FAS applies. Best to avoid FAS, do the install under L&I electrical
Remember the FAS inspection if you mount it on the house.

I'd rather change out the pedestal for a standard main breaker 3r panel and throw the standard meter on an Hframe. They make standard 3r panels with interlocks available.
 
Existing 200A meter/service pedistal at mobile home, with 3 breaker slots for branch ckts
Would this work?
Install a 200 A feed thru panel 8/16 ckts
Mount on outside of mobile home
Run feed from existing meter service to this new feed thru panel, and refeed mobile home
Install interlock kit on new 200 A feed thru panel with genny inlet
This minimizes outage and no dealing with poco
Thanks, I have only done 2 mobile home services 40 years ago
Why not mount it next to the meter pedestal instead of the MH?
 