Should I bond the ground and neutral for a double through manual transfer switch for a generator
Sent from my SM-G920T using Tapatalk
Sent from my SM-G920T using Tapatalk
If you dfo as such how many points will the neutral be bonded to the EGC then? If the neutral is grounded at both the SE as well as the genset at the same time there would be an issue.Should I bond the ground and neutral for a double through manual transfer switch for a generator
Sent from my SM-G920T using Tapatalk
Then answer is no... and the neutral should not be switched... and the neutral and ground at the generator should be isolated.It's being fed straight from an MDP where my neutral and ground are already bonded