T travislsuttle Member Location US Feb 18, 2016 #1 Should I bond the ground and neutral for a double through manual transfer switch for a generator Sent from my SM-G920T using Tapatalk
Should I bond the ground and neutral for a double through manual transfer switch for a generator Sent from my SM-G920T using Tapatalk
T templdl Senior Member Location Wisconsin Feb 18, 2016 #2 travislsuttle said: Should I bond the ground and neutral for a double through manual transfer switch for a generator Sent from my SM-G920T using Tapatalk Click to expand... If you dfo as such how many points will the neutral be bonded to the EGC then? If the neutral is grounded at both the SE as well as the genset at the same time there would be an issue.
travislsuttle said: Should I bond the ground and neutral for a double through manual transfer switch for a generator Sent from my SM-G920T using Tapatalk Click to expand... If you dfo as such how many points will the neutral be bonded to the EGC then? If the neutral is grounded at both the SE as well as the genset at the same time there would be an issue.
T travislsuttle Member Location US Feb 18, 2016 #3 It's being fed straight from an MDP where my neutral and ground are already bonded Sent from my SM-G920T using Tapatalk
It's being fed straight from an MDP where my neutral and ground are already bonded Sent from my SM-G920T using Tapatalk
Smart $ Esteemed Member Location Ohio Feb 18, 2016 #4 travislsuttle said: It's being fed straight from an MDP where my neutral and ground are already bonded Sent from my SM-G920T using Tapatalk Click to expand... Then answer is no... and the neutral should not be switched... and the neutral and ground at the generator should be isolated.
travislsuttle said: It's being fed straight from an MDP where my neutral and ground are already bonded Sent from my SM-G920T using Tapatalk Click to expand... Then answer is no... and the neutral should not be switched... and the neutral and ground at the generator should be isolated.