So Customer has a little 7400 watt genterator that will be feeding the panel with a https://www.platt.com/platt-electri...iance-Controls/PBN30/product.aspx?zpid=841282 and a interlock for the main and the 2-30 amp breaker.
Does 702.4(B)(1) when it says" user shall be permitted to select the loads connected". Does that mean they can just turn on and off the breakers they Want? or do I have to put all the loads they want through this https://www.platt.com/platt-electri...iance-Controls/R306A/product.aspx?zpid=181526
I was planning on making a List of Breakers that can be turned on and mounting in the panel.
He just wants his well pump 1hp 240Volt and fridge.
I have seen them both ways around here.
Thanks for the help
Does 702.4(B)(1) when it says" user shall be permitted to select the loads connected". Does that mean they can just turn on and off the breakers they Want? or do I have to put all the loads they want through this https://www.platt.com/platt-electri...iance-Controls/R306A/product.aspx?zpid=181526
I was planning on making a List of Breakers that can be turned on and mounting in the panel.
He just wants his well pump 1hp 240Volt and fridge.
I have seen them both ways around here.