Marc is right. There are lots of easier cheaper ways to do this.mdshunk said:Are you open to other design options that can be way cheaper and easier than a NEMA 3R manual transfer switch?
Marc is right. There are lots of easier cheaper ways to do this.mdshunk said:Are you open to other design options that can be way cheaper and easier than a NEMA 3R manual transfer switch?
RUWired said:230.94 Relative Location of Overcurrent Device and Other Service Equipment
The overcurrent device shall protect all circuits and devices.
Exception No. 1: The service switch shall be permitted on the supply side.
IMO the exception would not include a "transfer switch" as a service switch.
suemarkp said:Why not, isn't that what it does (switch to service 1, service 2, or off)?
suemarkp said:Still can't agree with your interpretation. So its Service1, Off, Feeder/Something else. It still switches out the service.
iaov said:Marc is right. There are lots of easier cheaper ways to do this.
Sorry, didn't realize I responded to this thread, and didn't check back. I was thinking of things like the 3rd party "InterlocKit" as well as just subfeeding a small "emergency panel" with a backfed "generator breaker" in the main panel with the panel manufacturer's see-saw type interlock between the subfeed breaker and the backfed generator breaker. A service rated outdoor transfer switch certainly is a sexy way to do a generator hookup, but it's also the most expensive.frizbeedog said:...and you two are going to keep us on pins and needles for how long, eaxactly? Or is this the so called dramatic pause before the climax?
Drum roll please.
RUWired said:Mark, I agree it would all work but, how do you get past 230.94.You would be putting an entire generator system before the main OCPD. Unless you can convince the inspector that when switch in the gen mode, the main is now part of the gen circuit, but that would make it a sds then.