M mayor43822 Member Jul 9, 2008 #1 is there an exception to art. 550.33 which would allow SER cable to be used for feeder cable for a manufactured home ( double wide )
is there an exception to art. 550.33 which would allow SER cable to be used for feeder cable for a manufactured home ( double wide )
wbalsam1 Senior Member Location Upper Jay, NY Jul 9, 2008 #2 mayor43822 said: is there an exception to art. 550.33 which would allow SER cable to be used for feeder cable for a manufactured home ( double wide ) Click to expand... The feeder conductors coming from the disconnect to the double-wide must have an insulated equipment grounding conductor. That would rule out the typical 4-wire SER.
mayor43822 said: is there an exception to art. 550.33 which would allow SER cable to be used for feeder cable for a manufactured home ( double wide ) Click to expand... The feeder conductors coming from the disconnect to the double-wide must have an insulated equipment grounding conductor. That would rule out the typical 4-wire SER.