MANUFACTURED HOUSE AND 120% RULE

ING23

Member
Location
Las Vegas
Occupation
Site Survey Tech
THIS PARTICULAR SCENARIO IS IN MOST MANUFACTURE HOME AT LEAST IN NEVADA, WHERE YOU HAVE A STAND ALONG OR PEDESTAL METER , SOME TIME INSIDE THIS PEDESTAL THERE IS MAIN LOG OR A MAIN BREAKER WITH MORE SPACE FOR OTHER BREAKERS. ONE OF THIS BREAKER FEED THE SUB INSIDE THE HOUSE WHERE ALL BRANCH CIRCUITS ARE DISTRIBUITED. THIS SUB HAS IT IS OWN MAIN BREAKER (SEPARATE BUILDING ) AND ITS OWN BUS RATING. SORRY FOR THE DELAY ..... HERE IS THE QUESTION. ....DOES THE 120% RULE HAS TO APPLY TO THE HOUSE SUBPANEL , STAND ALONG (PEDESTAL ) OR BOTH?
 

Attachments

  • FORUM.JPG
    FORUM.JPG
    247.9 KB · Views: 7

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(a) Please, no caps
(b) What 120% rule ?? (There is a 125% rule for continuous loads which does not apply here)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
(a) Please, no caps
(b) What 120% rule ?? (There is a 125% rule for continuous loads which does not apply here)

He is talking solar where you can size the solar input to 120% of the main buss. A 200 amp panel would mean 240 amps---40 amps solar.
 