In chapter 9 Note to the table it states the following:
(4) Where conduit or tubing nipples having a maximum
length not to exceed 600 mm (24 in.) are installed between
boxes, cabinets, and similar enclosures, the
nipples shall be permitted to be filled to 60 percent of
their total cross-sectional area, and 310.15(B)(3)(a) adjustment
factors need not apply to this condition.