mkgrady
Senior Member
- Location
- Massachusetts
I'm preparing a bid to disconnect and reconnect a bunch of docks at a marina in Massachusetts. The marina is going to be dredged and the floats are in the way. Three 270' docks (A,B & C) will be seperated at some of the existing float joints at the closest junction box. I see what looks like problems on some of the docks' existing wiring and I could use advice.
Dock A feeds 8 old hubbell pedestals with double 20 amp receptacles in each. Doesn't the code require 30 amp for boats? Are in-use covers required?
I think I have to rewire the dock when it gets put back together because the feeder that runs down the dock (above the flotation blocks and under the deck boards) is 1/0 thhn/thwn in PVC but it goes to open wire at the float joints so the dock can flex. Open wire with some kind of fabric for protection seems like a code violation??? The PVC runs to a PVC junction box under the deck boards where each pedestal is tapped in with a smaller cable in a smaller PVC conduit. Doesn't the code prohibit a splice under the deck? If allowed, is a JB under the wooden deck boards considered accessable?
I'm concerned that if I have to run all new cable I will have to upgrade the pedestals too.
Dock B has similar problems except the pedestals have 30 amp receptacles. But here they didn't use any conduit or junction boxes at all, just open wire and open splices inder the deck?
Dock C seems to be newer and better. Type W multi cable as the main with smaller cable to the peds but the splices are still under the deck of the floats. Is this OK???
I'd really appreciate any input. I've wired shipyards that were already designed but I haven't wired a marina in over 20 years
Thanks, Mike
Dock A feeds 8 old hubbell pedestals with double 20 amp receptacles in each. Doesn't the code require 30 amp for boats? Are in-use covers required?
I think I have to rewire the dock when it gets put back together because the feeder that runs down the dock (above the flotation blocks and under the deck boards) is 1/0 thhn/thwn in PVC but it goes to open wire at the float joints so the dock can flex. Open wire with some kind of fabric for protection seems like a code violation??? The PVC runs to a PVC junction box under the deck boards where each pedestal is tapped in with a smaller cable in a smaller PVC conduit. Doesn't the code prohibit a splice under the deck? If allowed, is a JB under the wooden deck boards considered accessable?
I'm concerned that if I have to run all new cable I will have to upgrade the pedestals too.
Dock B has similar problems except the pedestals have 30 amp receptacles. But here they didn't use any conduit or junction boxes at all, just open wire and open splices inder the deck?
Dock C seems to be newer and better. Type W multi cable as the main with smaller cable to the peds but the splices are still under the deck of the floats. Is this OK???
I'd really appreciate any input. I've wired shipyards that were already designed but I haven't wired a marina in over 20 years
Thanks, Mike