Why NEC 2017 does not ask for marina installations isolating transformer (Straying currents, HV-MV faults) and GFCI devices for all circuits in LV distribution panels?

Thanks,

Andrew
 

Attachments

  • 12.4kV neutral.jpg
    12.4kV neutral.jpg
    15.9 KB · Views: 1

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I found this

555.4 Distribution System. Yard and pier distribution systems
shall not exceed 1000 volts phase to phase.


And this


555.5 Transformers. Transformers and enclosures shall be
specifically approved for the intended location. The bottom of
enclosures for transformers shall not be located below the electrical
datum plane.
 

Andy35

Member
Location
New York USA
That is a big issue, connection between MV neutral and LV neutral allows that the ground fault current in a distribution station 34.5/12.47kV (in vicinity of Marina) on 34.5kV side fault located before the fuse) will flow mostly through boat and water (lower resistivity than soil) and it could produce voltages which could be dangerous to the people and currents which could melt ground wire (7.2kV makes similar issue) . That is a reason why I, for time being, suggest an improved Wisconsin dairy connection and in the future an improved Southern Californian solution. On the low voltage side we need GFCI for all circuits.

Thanks,

Andrew
 

Andy35

Member
Location
New York USA
That could a big issue, I.e. connection between MV neutral and LV neutral allows that the ground fault current in a distribution station 34.5/12.47kV (in vicinity of Marina) on 34.5kV side fault (located before the fuse) will flow mostly through the boat and the water (lower resistivity than soil) and it could produce voltages which could be dangerous to the people and currents which could melt ground wire (7.2kV ground fault causes a similar issue, but probably lower LNPR)) . That is a reason why I, for time being, suggest an improved Wisconsin dairy connection and in the future an improved Southern Californian solution. On the low voltage side we need GFCI for all circuits.

As I know in many EU countries GFCIs have been used in all circuits even sometimes for the panel main CB.

Also MV ground is isolated from LV neutral and I have never heard that they had ESD.

Thanks,

Andrew
 

topgone

Senior Member
That could a big issue, I.e. connection between MV neutral and LV neutral allows that the ground fault current in a distribution station 34.5/12.47kV (in vicinity of Marina) on 34.5kV side fault (located before the fuse) will flow mostly through the boat and the water (lower resistivity than soil) and it could produce voltages which could be dangerous to the people and currents which could melt ground wire (7.2kV ground fault causes a similar issue, but probably lower LNPR)) . That is a reason why I, for time being, suggest an improved Wisconsin dairy connection and in the future an improved Southern Californian solution. On the low voltage side we need GFCI for all circuits.

As I know in many EU countries GFCIs have been used in all circuits even sometimes for the panel main CB.

Also MV ground is isolated from LV neutral and I have never heard that they had ESD.

Thanks,

Andrew