Hi,

I am having trouble figuring this out, or if its even doable. Maybe there is an all in one device I havent come across. My client would like all of their lighting controlled via a time clock and contactors. Simple enough. However, they would like to have a master switch to override the timeclock. How can I accomplish this without killing power to the timeclock and messing it up?
 

crispysonofa

Senior Member
Location
New England
Occupation
Electrical and Security Contractor
I am assuming you are using a line voltage timer. All you need to do is use a single pole switch (single phase) that energizes the load side of the time clock. It must be on the same circuit as the time clock feed. If you are using other than 120v you may need to use a double pole or triple pole switch respectively.
 

MattS87

Senior Member
Location
Yakima, WA
Hi,

I am having trouble figuring this out, or if its even doable. Maybe there is an all in one device I havent come across. My client would like all of their lighting controlled via a time clock and contactors. Simple enough. However, they would like to have a master switch to override the timeclock. How can I accomplish this without killing power to the timeclock and messing it up?

A 3-way switch will work for you. Use the common screw to your contactor, then connect the load side of your timers to one of the switch legs and 120V to the other
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Casualsparky did not say whether the override was to turn lights on, turn them off, or both (three position switch required for the latter.)
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
180131-2149 EST

More of the desired logic needs to be defined.

Suppose you have a light that is normally controlled by some timer or other source, and in addition you want manual control.

You can use a GE RR relay or some other pulse controlled mechanically bi-stable relay.

Thr RR relay has two coils, one is SET and the other is RESET. After setting or resetting the relay it remains in its last state.

Any number of manual switches, or other sources can control the RR relay. Basically there are two wire ORed logic circuits. One is set and the other is reset.

Whatever was the last source to trigger the RR trlay defines the state of the light.

.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
180131-2350 EST

To add to my logic discussion.

This system could be setup to always allow manual control of ON and OFF. So if the time clock turned on the light, then any time after that time clock on time the manual switches could turn off and on the light as desired.

What to do when the time clock gets to its off time? It could turn the light off whether or not set by the time clock or manually, or it could be inhibited from turning off the light if the ON had been manually generated.

If the time clock turned on the light, then the manual switch could turn off the light. Or if the time clock turned on the light, then this could inhibit manual turn off during the on period of the time clock.

You could have some, but not all, of the manual switches have more or less complete control of the on-off function.

More complex functions can be added such as occupancy sensing, and/or amount of exterior light.

.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Casualsparky did not say whether the override was to turn lights on, turn them off, or both (three position switch required for the latter.)

Override should be in both logic sets and all possible settings: time clock controlled on and off, and desired on and off. Matt87 and crispysonofa, a single snap switch will not turn on the lights if the clock calls for them to be off, and a 3-way will not turn off the lights if the time clock calls for them to be on.

Simplest, cheapest way to achieve all 4 possible outcomes or choices that I see would be to use a 3 position switch like you mentioned or 2 regular switches, one from load side of the clock, and one from a permanent power source. They may need to be 2 pole if 208 or 240V like crispy brought up.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I think the simplest setup would be to combine the ideas mentioned using a 3-way and a single-pole switch like this:

Time clock always hot to maintain time setting. Connect load to terminal common of 3-way. One traveler terminal to clock output, other traveler terminal to one terminal of SP switch. Other terminal of SP switch to always-hot terminal feeding clock. 3-way switch marked Auto/Manual, SP switch marked Manual On/Off.

Another option is a center-off switch, connected as 3-way above without SP switch, common to load, second terminal to clock, third terminal to hot.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We always use ASCO 917's mechanically held lighting contactors with momentary time clocks and momentary override switches.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
180201-1107 EST

We have no clear definition of what is the desired logic.

I am having trouble figuring this out, or if its even doable. Maybe there is an all in one device I havent come across. My client would like all of their lighting controlled via a time clock and contactors. Simple enough. However, they would like to have a master switch to override the timeclock. How can I accomplish this without killing power to the timeclock and messing it up?

What does the following mean?
My client would like all of their lighting controlled via a time clock and contactors.
Suppose this is a building with many rooms and halls. Are the halls on the time clock? Do the halls have individual switches that can turn lights on, that is, override the time clock in the ON direction? Same for individual rooms, but possibly different criteria.

What is to happen if the override switch is not turned off? In a pulsed system the time clock could turn off the lights at its timed off time. But suppose a person is in a totally enclosed room, pulsed the lights on, but while the person is in the room the time clock pulses off the lights. The person is in the dark.

However, they would like to have a master switch to override the timeclock.
Override to ON or to OFF. Are there individual switches on different legs of the contactors?

How can I accomplish this without killing power to the timeclock and messing it up?
I think this was already answered. But it is simple. Just power the time clock from an independent always on power source, and use the time clock output contacts as an isolated contact set.

A precise definition of the desired logic of the system must be created, only then it is possible to design a circuit to accomplish the desired objective. So far there is not an accurate definition of what the system is to do, or what the system looks like.

.
 

crispysonofa

Senior Member
Location
New England
Occupation
Electrical and Security Contractor
Override should be in both logic sets and all possible settings: time clock controlled on and off, and desired on and off. Matt87 and crispysonofa, a single snap switch will not turn on the lights if the clock calls for them to be off, and a 3-way will not turn off the lights if the time clock calls for them to be on.

Simplest, cheapest way to achieve all 4 possible outcomes or choices that I see would be to use a 3 position switch like you mentioned or 2 regular switches, one from load side of the clock, and one from a permanent power source. They may need to be 2 pole if 208 or 240V like crispy brought up.

I was thinking that he would feed the switch from the line side of the clock thus it would energize the lights even if the clock was not calling for the lights to be on. I did not think about turning the lights off, I like the points that were brought up.
 
Sorry I left out alot of information. Lighting controls clearly are not my specialty. All the circuits are 120v/15a. The way I have wired it is that the 3 ccts share a common neutral. The client would like a time clock to turn on/off the lights in the building at programmed times. However, they would like an override switch in order to turn on the lights in the case that somebody is in early/ keep them off in the case that it is a holiday etc and nobody is in. I am not familiar with time clocks or contactors. I understand that I am able to use a 3 pole contactor for this purpose.. do I need a separate cct to power the coil? And would the time clock be single pole/ single throw? I love the i put but still struggling with the best way to accomplish this
 
All of the lights in the building are controlled by occupancy sensors and/or manual switches. All they wish to do is have them turn off at night and on in the morning. Except the given example exceptions I listed. So basically everything powered or everything off. But while keeping the power to the time clock.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
180220-2416 EST

Casualsparky:

Your new information is useful, but still not adequate.

About electromechanical relays (a contactor is just a relay). A relay consists of an isolated coil to create a controlled magnetic field to actuate an electrical contact. The coil voltage does not need to have any particular relationship to the voltage of the switched circuit. Quite often both voltages will be the same. These do not need to originate from the same source.

Your present system has a multitude of motion sensors and manual switches.

Based on a part of the description of what you want the following could be done:

1. After your breaker panel install a 3 pole contactor with normally open contacts to switch the 3 hot lines of your 3 circuits.

When this contactor is energized all your circuits will work like they do now.

When this contactor is de-energized, then there will be no available lights.

Control the contactor from a simple timer. This will always do the same thing every day.

To over-ride the timer connect a SPST manual switch in parallel with the timer contact. When this switch is closed the contactor is energized and your system will work like it does now. Under this closed condition the timer has no effect on the operation of the lighting system.

This has some disadvantages, but may be adequate.

.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
There is something to be said for constructing the override system using latching contactors and momentary pushbuttons:

If you use two static switches as in the most recent suggestion, then leaving one of the switches in the wrong position will override the time clock action indefinitely.

If instead you use the time clock to generate on and off pulses to a single latching contactor any override, either on or off, can be reversed at any point using the opposite button and in any case the next time clock set point activation will return to the normal schedule until the next override.
The disadvantage is that you cannot preset the on-override to prevent the time clock from turning off the lights but must instead turn the lights back on after the clock has turned them off.
Nor would it work for setting the lights to override off in advance of a long weekend. (You would also have to use a 7-day time clock to handle normal weekends properly.)
 

Jamesco

Senior Member
Location
Iowa
Occupation
Master Electrician
Sorry I left out alot of information. Lighting controls clearly are not my specialty. All the circuits are 120v/15a. The way I have wired it is that the 3 ccts share a common neutral. The client would like a time clock to turn on/off the lights in the building at programmed times. However, they would like an override switch in order to turn on the lights in the case that somebody is in early/ keep them off in the case that it is a holiday etc and nobody is in. I am not familiar with time clocks or contactors. I understand that I am able to use a 3 pole contactor for this purpose.. do I need a separate cct to power the coil? And would the time clock be single pole/ single throw? I love the i put but still struggling with the best way to accomplish this

Just parallel the contacts from this across the contacts of the time clock.

Simple to use, operator friendly, and the user sets the amount of override time he/she so chooses. It's even fail safe and restores control to the time clock after it times out.:):):)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Just parallel the contacts from this across the contacts of the time clock.

Simple to use, operator friendly, and the user sets the amount of override time he/she so chooses. It's even fail safe and restores control to the time clock after it times out.:):):)
That gives you override ON, but the OP also wants override OFF for off schedule days/times the building is not in use.
Add a second such timer with NC instead of NO and put it in series with the time clock contacts?

Sent from my XT1585 using Tapatalk
 