The NEC says transformers connected into a multi-phase "bank" are treated as a single transformer not as individual ones.
The NEC says transformers connected into a multi-phase "bank" are treated as a single transformer not as individual ones.
... it does seem wrong to me that if I connect a single phase 4:1 coil (no center tap) that I need a bigger conductor size than if I connect three identical coils to the same primary voltage via a common neutral point.
Yes, I noticed. And it IS material to the question. You keep coming up with with odd-ball scenarios like "240V : 24V/240V single phase transformers" to try to explain your point. Now it's a 25kVA, 480-120V single phase transformer with a rated secondary current of 208A, even though you started out needing "100A @ 120V."Notice I never specified the transformer size, as it's immaterial to this question. We can make it 25 kVA if you like.
How about connecting more than two or three sets of secondary conductors to the same transformer to serve separate loads? Is that ever done? (Is it not allowed?)Yes, I noticed. And it IS material to the question. You keep coming up with with odd-ball scenarios like "240V : 24V/240V single phase transformers" to try to explain your point. Now it's a 25kVA, 480-120V single phase transformer with a rated secondary current of 208A, even though you started out needing "100A @ 120V."
If you have to keep coming up with crazy scenarios instead of practical applications in order to get your point across, that might just be a hint that your point is wrong.
And the point is the minimum ampacity requirements should be the same for one 10kVA, 480-120V single phase transformer (83A rated secondary current), and three 10kVA 480-120V single phase transformer connect together D-Y (also 83A rated secondary current.)We're discussing the minimum ampacity requirements for secondary conductors. That's all.
How about connecting more than two or three sets of secondary conductors to the same transformer to serve separate loads? Is that ever done? (Is it not allowed?)
OK, this is at least on the face of it a plausible idea and is the most constructive thing you've said so far in response to the issue I've raised. To work out the math for those following along:And the point is the minimum ampacity requirements should be the same for one 10kVA, 480-120V single phase transformer (83A rated secondary current), and three 10kVA 480-120V single phase transformer connect together D-Y (also 83A rated secondary current.)
Hence my example in post #54 is practical, not oddball. The only oddball example I had I labeled as such (absurd was my term).Yes, it is done, and yes, you would follow the rules in the same way.
Why do you think that we should be allowed to have a larger primary OCPD, without increasing the minimum secondary conductor size?And the point is the minimum ampacity requirements should be the same for one 10kVA, 480-120V single phase transformer (83A rated secondary current), and three 10kVA 480-120V single phase transformer connect together D-Y (also 83A rated secondary current.)
...
One 10 kVA, 480V : 120V single phase transformer has a rated primary current of 20.8A and...
A 30 kVA, 480D : 208Y/120V 3 phase transformer (or 3 of the above single phase transformers in a D-Y configuration) ...
...
Make a comparison if you connect both the single phase and three phase transformer in the same manner, primary and secondary protected per T450.3, with the maximum allowed primary OCPD. Calculate the required minimum ampacity of the secondary conductors for each per 240.21(C)(6).
You will find that both transformers, which both have the same rated secondary current, also have the same required minimum secondary conductor ampacity (within some rounding.) And wouldn't you expect them to?
OK, you're wrong. : - ) In that you can't have the same current ratings on both primary and secondary for the single phase case and for the delta-wye case. [You could in a wye-wye with the same transformer as in the single phase case.]Correct me if I'm wrong but wouldn't the second transformer be rated 17.3kVA with the same current ratings?
Make a comparison if you connect both the single phase and three phase transformer in the same manner, primary and secondary protected per T450.3, with the maximum allowed primary OCPD. Calculate the required minimum ampacity of the secondary conductors for each per 240.21(C)(6).
You will find that both transformers, which both have the same rated secondary current, also have the same required minimum secondary conductor ampacity (within some rounding.) And wouldn't you expect them to?
BTW, this is the source of the issue in this discussion, and the reason for the limitation in 240.4(F).On the primary side, each delta line conductor is now attached to two transformers.
Took me a lot longer to write that up than 3 seconds.Can't believe you beat me to it by three seconds Wayne.
Not following what you mean by that?(What tripped me up, by the way, was not realizing that they actually regulate the protection of each coil by the secondary current rating rather than the primary rating.)
I see that language in 450.3 "Overcurrent Protection," but it is restricted to "as used in this section." Is there other language elsewhere that would make that true for purposes beyond 450.3?The NEC says transformers connected into a multi-phase "bank" are treated as a single transformer not as individual ones.
Industry standards are being disputed between a mathematician and an engineer.I don't think we've made any progress in the discussion here.
The highlighted is wrong. Therefore the math is wrong. Perhaps this is where you are going off the rails.OK, this is at least on the face of it a plausible idea and is the most constructive thing you've said so far in response to the issue I've raised. To work out the math for those following along:
One 10 kVA, 480V : 120V single phase transformer has a rated primary current of 20.8A and a rated secondary current of 83.3A. So the primary can be protected at 250% * 20.8A = 52.1A, round up to 60A OCPD (Table 450.3(A), Note 1), if the secondary is protected at 125%* 83.3A = 104.2A, round up to 110A OCPD maximum. With a 60A primary OCPD, the minimum 240.21(C)(6) secondary conductor ampacity is 60A * (480V/120V) / 3 = 80A. So if you needed, say, a 50A 120V circuit and a 60A 120V circuit, you could run two sets of secondary conductors up to 25' to side-by-side panelboards, one protected at 50A and one at 60A (Table 450.3(A), Note 2), but you'd need to use 80A conductors for each set.
And this is what is ridiculous. If you install a 30kVA, 480-208/120V transformer to supply a 100A MCB panel on the secondary side, the Code isn't telling you that you need to run a 120A conductor.A 30 kVA, 480D : 208Y/120V 3 phase transformer (or 3 of the above single phase transformers in a D-Y configuration) has a rated primary current of 36.1A and a rated secondary current of 83.3A. So the primary can be protected at 250% * 36.1A = 90.2A, I'll say we have to round to 90A before rounding up, which puts the maximum primary OCPD at 90A, provided again our secondary OCPD is no more than 125% * 83.3A = 104.2A, round up to 110A OCPD maximum. Then with a 90A primary OCPD, if we say the voltage ratio is 480/208, the minimum 240.21(C)(6) secondary conductor ampacity is 90A * (480V/208V) / 3 = 69.3A. While if we say the voltage ratio is 480/120, the minimum secondary conductor ampacity is 90A * (480V/120V) / 3 = 120A.
Ah, thank you. I was looking at Table 450.3(A) instead of 450.3(B), and in 450.3(B), Note 1 on rounding up only applies some of the time, and not to the primary OCPD with using primary + secondary protection.The highlighted is wrong.
As a difference in rounding, the change is minor and is unrelated to what we are debating. The correction:Therefore the math is wrong. Perhaps this is where you are going off the rails.
Or you could do something practical and run the secondary to a 100A mcb panelboard."So the primary can be protected at 250% * 20.8A = 52.1A, round down to 50A OCPD (Table 450.3(B), Note 1 does not apply), if the secondary is protected at 125%* 83.3A = 104.2A, round up to 110A OCPD maximum (Note 1 does apply). With a 50A primary OCPD, the minimum 240.21(C)(6) secondary conductor ampacity is 50A * (480V/120V) / 3 = 66.7A. So if you needed, say, a 50A 120V circuit and a 60A 120V circuit, you could run two sets of secondary conductors up to 25' to side-by-side panelboards, one protected at 50A and one at 60A (Table 450.3(A), Note 2), but you'd need to use 67A conductors for each set."
Why shouldn't it if your primary OCPD is at 250%? If you don't want to have to oversize the secondary conductors, don't oversize the primary OCPD, which is the only thing protecting those secondary conductors from short circuit/ground fault. Or stick with the 10' rule, 240.21(C)(2), which allows a 10:1 ratio instead of a 3:1 ratio.And this is what is ridiculous. If you install a 30kVA, 480-208/120V transformer to supply a 100A MCB panel on the secondary side, the Code isn't telling you that you need to run a 120A conductor.