That is correct. Wire types not listed in that table are not permitted for NEC applications. (Note that Table 310.104 became Table 310.4(A) in the 2020 code)In mikes dvd he said dlo was not in 310 104 A so it cant be used. Is that right?
That being said, there is dual rated DLO on the market. It rated DLO/RHW and with that rating it can be used for NEC applications. The ampacity would be based on Table 310.16 for that use, however, the 2020 code with new language in 310.15(A) permits the interpolation of ampacities for non-standard conductor sizes under engineering supervision.
310.15(A) ... Under engineering supervision, ampacities of sizes not shown in ampacity tables for conductors meeting the general wiring requirements shall be permitted to be determined by interpolation of the adjacent conductors based on
the conductor’s area.