Typically you don't see Fuse Only on the units except for commercial units or older residential units. Fuse tend to react faster then breakers I believe but I am not sure why that is so important with some units.
95% or more of the A/C units I inspect will allow fuse or HACR circuit breakers for the MOCP per the manufacturer specs. Ofter-time the use of a breaker is a (*) footnote.
Most of the walk-in coolers and freezers units i inspect are "Fuse" or "Fuse Only".
I'd say on commercial jobs the drawings I see are 50/50 fusible or non-fusible disconnects. Some contractors use fusible ones to facilitate quick adaption in the event the new units arrive specifying other size OCP than expected.