Hey all,
Thanks in advance for the help..
I'm feeding a 3 phase 208 rooftop unit, and the closest junction box with 208 is about 15 feet away...
I'd like to run 3/4" Sealtite from the disconnect on the roof to the junction box, but am unsure what article lists the max length of liquidtight i can use.
I remember a certain article that states if the liquidtight is over 6', it needs a separate grounding wire, which is fine, but can't find the rest..
???
Thanks in advance for the help..