Max ocpd for abb vfd

darekelec

Senior Member
Location
nyc
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
 

Attachments

  • IMG_2663.jpeg
    IMG_2663.jpeg
    676.5 KB · Views: 24
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
Read the fine manual.

Eta: You may need to be using fuses. The breaker could stay but fusing or other protective device will need to be installed. RTFM
 
Last edited:
What size breaker would be a minimum sufficient to run this motor? It’s air handling fan on a roof.
 

Attachments

  • IMG_2691.jpeg
    IMG_2691.jpeg
    1.2 MB · Views: 13
Vfd is 88 amp max , motor is 80 amp max .
Is 100 amp breaker gonna be enough?
Will it be operating at full load most of the time, or practically never?
Code requires 125% of its, the VFD, rating for the conductors to it. Will the 100 amp breaker work? Most likely.

Read the fine manual because you may need specified protection ahead of it somewhere.
 
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
You can keep the 200 amp circuit breaker if you install a fused safety switch or and
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
You could keep the 200 amp circuit breaker as long as you install a fused safety switch or a circuit breaker . Going by the ABB chart it should be a 150 amp circuit breaker. I'm old school and for over 90% of the motors that I wired up over 50 years liked to only go 125% over nameplate Amps who!e using quality 200 KIAC rated time delay fuses. On numerous drives without bypasses this 125% thinking never failed as on all the drives that I installed or worked on had at least a ten second ramp up time greatly reducing inrush current. On centrifuges that took over 20 seconds to reach full speed & air compressors & refrigerant compressors had to usually go with 175% of motor FLA. For a drive rated for 88 amps output and no bypass I would use 110 amp time delay fuses.I have installed VFD'S for 40 to 125 HP fans using the 125% sizing with no problem. I always ordered drives with built in disconnect switch and input fuses.
I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?

I have a situation where contractor run 200 amp wire and breaker to a starter of 30 hp motor.
I am swapping the starter for abb vfd.
Can I keep the 200 amp breaker or should I replace it with smaller?
 
The said drive has bypass.
Now what?
30HP 230V, NEC table says 80A, 430.52 says CB is max. 250%, 80 x 2.5 = 200A. Good to go for the bypass...
So now your only problem is that the VFD cannot have a 200A breaker ahead of it. So what you do is put 150A FUSES downstream of the breaker, but ONLY ahead of the VFD.
 