Carultecl...Cool, thanks. I've tried an example calculation, and the three delta-side line currents do not add up to zero. A delta transformer doesn't connect to the neutral. So if this delta primary were supplied from another WYE system, how would the WYE system supply this imbalance?
Example calculation:
Ias = 100A
Ibs = 90A
Ics = 80A
Iap = 41.2
Ibp = 36.8
Icp = 39.1
**This does not add up to zero, but adds up to 3.75A that would ordinarily be on the neutral.
My calcs are based on a step-down, D-Y Xfmr, serving a 3-ph, 4w panel!
**What are the pf angles in your example?
Will do calc base on your sec'y load-currents assuming unity-pf!
Phil