Max receptacle height

Status
Not open for further replies.

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
Is there a maximum height for a convenience receptacle in a commercial hallway? If considered electrical equipment, max would be 6' 6", but that could possibly be stretching a definition.....
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No maximum unless it's being counted as the required wall space receptacles in a dwelling then the max is 5'6".
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
An outlet is not required in a hallway in a commercial building. After that, it doesn't really matter.
Put it where you want.
 