(B) Class I, Division 2 In Class I, Division 2 locations, all utilization equipment shall comply with 501.135(B)(1) through (B)(3).
(1) Heaters Electrically heated utilization equipment shall conform with either item (1) or (2):
(1) The heater shall not exceed 80 percent of the ignition temperature in degrees Celsius of the gas or vapor involved on any surface that is exposed to the gas or vapor when continuously energized at the maximum rated ambient temperature. If a temperature controller is not provided, these conditions shall apply when the heater is operated at 120 percent of rated voltage.
Exception No. 1: For motor-mounted anticondensation space heaters, see 501.125.
Exception No. 2: Where a current-limiting device is applied to the circuit serving the heater to limit the current in the heater to a value less than that required to raise the heater surface temperature to 80 percent of the ignition temperature.
(2) The heater shall be identified for Class I, Division 1 locations.
Exception: Electrical resistance heat tracing identified for Class I, Division 2 locations.