I have a feeder off the outdoor panel to 2- 30 amp pedestals. The farthest one if I run number #8 makes my total vd back to meter total of %6.38VD
if I run #6 %5.8VD. I know combined with Feeder and Branch should not be more than %5.
at 120volt with 6.38 I have a lose of 7.65volts so I ll be at 112.35 volts.
I am trying to find if the RV has a tolerance of +/- 10% like most equipment I have dealt with.
I have to do plan review with the county since I " touched the conductor". They told me there looking for VD issue. Though I don't know how they can enforce them unless the RV has a tighter tolerance.
No local Amendments that I am aware of.
Any help would be appreciated.