We have twelve legacy #12 conductors in underground 3" pipe, and are looking to maximize the ampacity.
We had hoped to replace this conduit, but the local sewer district denied a request to cross their 9 foot deep clay sewer, without buying them a new HDPE sewer.
Is there a better strategy for utilizing these conductors?
The service is 3 phase 120/208Y.
The 3” conduit has twelve AWG #2 THWN-2 copper, and two AWG #6 THWN-2 copper.
No parallel conductor option (as parallel conductors under 360Hz are allowed at 1/0 AWG and larger only [ NEC 310.10(G)(1) ] )
Terminals are 75C.
All loads are continuous (EV charging).
Voltage drop based on distance is not a concern (EV charging: the cars can adapt).
No local shunt trip requirement for EV.
No neutral required.
Local soil temperature at 18" depth is 15-19°C max all year (10% adder).
Options?
Use
3 conductors 90C rating one 130A three phase run, no capacity derating, limit to 115A based on terminals (115A total).
6 conductors 90C rating two 130A runs, 80% derating, 104A each (208A total)(Two 100A breakers).
9 conductors 90C rating three 130A runs, 70% derating, 91A each (273A total)(270A net w/90A breakers).
12 conductors 90C rating four 130A runs, 50% derating, 65A each (256A total)(Um next size up rule 70A x 4 = 280A per 240.6(A)).
We had hoped to replace this conduit, but the local sewer district denied a request to cross their 9 foot deep clay sewer, without buying them a new HDPE sewer.
Is there a better strategy for utilizing these conductors?
The service is 3 phase 120/208Y.
The 3” conduit has twelve AWG #2 THWN-2 copper, and two AWG #6 THWN-2 copper.
No parallel conductor option (as parallel conductors under 360Hz are allowed at 1/0 AWG and larger only [ NEC 310.10(G)(1) ] )
Terminals are 75C.
All loads are continuous (EV charging).
Voltage drop based on distance is not a concern (EV charging: the cars can adapt).
No local shunt trip requirement for EV.
No neutral required.
Local soil temperature at 18" depth is 15-19°C max all year (10% adder).
Options?
Use
3 conductors 90C rating one 130A three phase run, no capacity derating, limit to 115A based on terminals (115A total).
6 conductors 90C rating two 130A runs, 80% derating, 104A each (208A total)(Two 100A breakers).
9 conductors 90C rating three 130A runs, 70% derating, 91A each (273A total)(270A net w/90A breakers).
12 conductors 90C rating four 130A runs, 50% derating, 65A each (256A total)(Um next size up rule 70A x 4 = 280A per 240.6(A)).