I need to know what is maximum unbalance (total Load) is OK without any trouble to a 3-phase LV transformer.
I have 30KVA Delta-star (480/380/220) Transformer, on which only a single equipment of three phase 380V- 20KW is connected, and I need to connect a single phase (220V- 3.3KW load on any of the phase on star/secondary.
Is that unbalance is allowable.
Thanks
 
Probably.

That one phase will be fully loaded but not overloaded.

The imbalance might impact voltage balance, and that could impact the balanced load
 
You can treat the secondary as if it was three single transformers, each with 1/3 the capacity of the full rating. In your case you have (3) 10kVA single phase transformers that can be loaded any way you want.
 