I have a multiplex trailer with 8 "plexes", each or which has its own panel. It's treated as a single building.
The building will be fed by a switchrack, which has a common 1200A bus. There are 8 circuit breakers connected to the bus, each of which feeds one panel on the trailer.
The switchrack has a main breaker. A feed from the utility goes directly to the main breaker. Switchrack is located within 20 feet of the trailer. Switchrack is de-energized by opening the main breaker.
Articles 225.30 and 225.33(A) have come up.
QUESTION: Are we in violation of these articles, or does the service from the utility count as a single supply, and the main breaker serve as a single disconnecting means?
Articles for your reference:
NEC Article 225.33(A) Maximum Number of Disconnects: “The disconnecting means for each supply permitted by 225.30 shall consist of not more than 6 switches or six circuit breakers mounted in a single enclosure... "
225.33(A), it references Article 225.30 Number of Supplies, which states in part “A build or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder unless permitted by 225.30(A) through (E). For the purposes of this section, a multiwire branch circuit shall be considered a single circuit.