Okay, I have a little update.
The utility company has confirmed the utility gear (what I called) within the building is customer owned but the utility has a lock on the main disconnect which that something I can't comprehend! now my questions is, can you have a lock on the main service disconnecting mean? I'm reading NEC230.92 which it appears we can.
230.92 Locked Service Overcurrent Devices. Where the service
overcurrent devices are locked or sealed or are not readily
accessible to the occupant, branch-circuit or feeder overcurrent
devices shall be installed on the load side, shall be mounted in a
readily accessible location, and shall be of lower ampere rating
than the service overcurrent device.
As was said earlier, this main disconnect feed another switchgear with 7 disconnects. If I do understand it correctly, 230.92 means we can open all the 7 disconnects which we still in compliance with 230.92. Is my interpretation correct?
Thanks,
The utility company has confirmed the utility gear (what I called) within the building is customer owned but the utility has a lock on the main disconnect which that something I can't comprehend! now my questions is, can you have a lock on the main service disconnecting mean? I'm reading NEC230.92 which it appears we can.
230.92 Locked Service Overcurrent Devices. Where the service
overcurrent devices are locked or sealed or are not readily
accessible to the occupant, branch-circuit or feeder overcurrent
devices shall be installed on the load side, shall be mounted in a
readily accessible location, and shall be of lower ampere rating
than the service overcurrent device.
As was said earlier, this main disconnect feed another switchgear with 7 disconnects. If I do understand it correctly, 230.92 means we can open all the 7 disconnects which we still in compliance with 230.92. Is my interpretation correct?
Thanks,