Be nice to us uneducated sorts. What is a (are?) "polemics"?... besides of engaging in polemics.....
ice
Be nice to us uneducated sorts. What is a (are?) "polemics"?... besides of engaging in polemics.....
Be nice to us uneducated sorts. What is a (are?) "polemics"?
ice
As the OP did state he would be utilizing a VFD the minimum sized transformer capacity requirement would typically be 500 kVA. If the application did allow for ACTL starts then a larger capacity would be required - but there are thousands of VFDs at 500 hp that are powered through 500 kVA isolation transformers. You could in fact purchase a PF7000 or PF750 with as integrated transformer (step-up, step-down, whatever you need) & Rockwells initial sizing for 500 hp would be around 500-600 kVA for that. If the existing 480 transformer and gear have capacity for at least 500 kVA I would have zero problems with adding a 500 hp motor on a VFD if that was a pump type application. If it were a high torque app that required 150% (or more) torque for long periods like a big conveyor then I would use a 600 to 750 KVA isolation (or capacity need on existing). If you have to add additional transfomer capactity for this application I would price out all the requirements to see if you go PF7000 or PF750, it may surprise you. I have done as high as 700 hp on a 480 volt Rockwell 1336 Impact & have also done some 400 HP 4 kV PF7000's & last month a 400 hp 480 volt PF755 at the same location. The last time I checked the break-over from a total cost stand point was around 750-800 hp. Above that point 4 kV was cheaper, but it will vary depending on current copper costs.
The cost of VFD may be equal or more than the cost of the motor itself. If cost consious, other options may be explored as is being done in previous posts.
It has nothing to do with it, because it was not the answer to it.What does this have to do with the question you were directly asked?
I do not know. You may contact the publisher or the authors of the book mentioned in post # 52 for further details.I will ask it again.
WHERE IN THE NEC IS THERE A MINIMUM SIZING REQUIREMENT ON TRANSFORMERS?
I do not know. You may contact the publisher or the authors of the book mentioned in post # 52 for further details.
I made the statement. No doubt in it. I also stated on what basis I made it. I also suggested to refer to the source for further details. There is no integrity issue here. Just a fault finding mentality involved here.....Except it was you who made that statement and now you're diverting again and attribute it on somebody else. No integrity....
I made the statement. No doubt in it. I also stated on what basis I made it. I also suggested to refer to the source for further details. There is no integrity issue here. Just a fault finding mentality involved here.....
80% rule for equipment capacity is not there in NEC. But NEC does recommend spare capacity and I think 80% rule for equipment capacity is based on it.
An 80% rule is just the inverse of one of many 125% rules.....where is this found in the NEC?
I did a search for 80% and did not find it used in this context anywhere in the code.
An 80% rule is just the inverse of one of many 125% rules.....
Of course, the NEC has not so far made any spare capacity as a mandatory rule. However it has made it as a recommendation till date ( see its information note in post#51.).in the NEC, there are no rules that require any spare capacity at all.