There is no general rule that says that.
You can load anything to 100% non-continuos.
Yes, but consider a continuous load with MD of 80 KVA. What is the minimum capacity of transformer? Is not equal to 80x1.25=100KVA?
There is no general rule that says that.
You can load anything to 100% non-continuos.
Yes, but consider a continuous load with MD of 80 KVA. What is the minimum capacity of transformer? Is not equal to 80x1.25=100KVA?
The minimum NEC rating of a transformer with 80KVA of continuous load is 80 KVA.
There is no NEC '80% rule' for transformers.
You are complying with 90.1(B) :thumbsdown:.
Nope, 90.1(B) has nothing to do with my response.
How about this, how about you post the NEC code section you believe requires a transformers load to be under 80% OR you just drop this silliness?![]()
I have to quote also the same 90.1(B), which recommends spare capcity to be built into an electrical equipment.
I do not know what is silly about this.
Oh! the topic deals about electrical design aspects about which you appear to know not very much.
No.Now you are changing the topic.
Is the topic what the NEC requires or is the topic what a good design should include?
Pick a topic, stick with it and we can discuss, if you want to keep jumping between topics you will be discussing it with yourself.
Fantastic response, if you can't prove your point try to change the subject. :thumbsup:
The NEC also says it is NOT a design manual, and anyway, nothing in article 90 is enforceable.
I think you are making a logic leap from conductor ampacity requirements and OCPD requirements to transformer sizing that just is not found in the code.
Yes, but consider a continuous load with MD of 80 KVA. What is the minimum capacity of transformer? Is not equal to 80x1.25=100KVA?
The topic is what the NEC recommends to include in a good design (90.1B), which every one here knows. So stop kidding.
90.1 Purpose.
(B) Adequacy. This Code contains provisions that are considered
necessary for safety. Compliance therewith and
proper maintenance results in an installation that is essentially
free from hazard but not necessarily efficient, convenient,
or adequate for good service or future expansion of
electrical use.
Informational Note: Hazards often occur because of overloading
of wiring systems by methods or usage not in conformity
with this Code. This occurs because initial wiring
did not provide for increases in the use of electricity. An
initial adequate installation and reasonable provisions for
system changes provide for future increases in the use of
electricity.
I think you are making a logic leap
As I said demonstarting a fundamental lack of uderstanding of what the Code is, what purpose it serves and how it is supposed to work. Makes me wonder what interest somebody from India and the telcom industry have in the NEC that is not aplicable to their filed of work, besides of engaging in polemics.....
I am from India and working as an electrical engineer in Telecom Industry.
I decided to assess the worth of NEC and the guys using it.....
. Just joking.
There are, of course, some commonalities between American and Indian Electrical Systems. I just
want to learn and to better grasp the common working principles.
Thanks.
Really?you know it all.........
Not really me. See table 2.2 on page no.2-10 of the book (after purchasing it, of course)
http://books.google.co.in/books/abo...ower_systems.html?id=k-NSAAAAMAAJ&redir_esc=y
In the above book the authors are really making the 'leap' and it is a correct one as far as the OP is concerned.
Not really me. See table 2.2 on page no.2-10 of the book (after purchasing it, of course)
http://books.google.co.in/books/abo...ower_systems.html?id=k-NSAAAAMAAJ&redir_esc=y
In the above book the authors are really making the 'leap' and it is a correct one as far as the OP is concerned.
For a maximum size of 500 hp motor, minimum transformer size is 2.5 MVA at 480V . The total load shall not exceed 2.0 MVA per NEC.
weressl & petersonra:
Our main contention is the content of the second sentence below
I based both the sentences from that book just to help the OP.
weressl & petersonra:
Our main contention is the content of the second sentence below
"
For a maximum size of 500 hp motor, minimum transformer size is 2.5 MVA at 480V . The total load shall not exceed 2.0 MVA per NEC."
I based both the sentences from that book just to help the OP.