Is there a maximum run for flex conduit in indoor applications?

I've never used the stuff before and I never noticed any tables in my reference books, but there's got to be a limit right?.
 

TOOL_5150

Senior Member
Location
bay area, ca
Is there a maximum run for flex conduit in indoor applications?

I've never used the stuff before and I never noticed any tables in my reference books, but there's got to be a limit right?.

THe only limit is being able to actually pull conductors through the conduit. Remember FMC has a 360 degree max and every little bend, technically, counts. So, basically no, there is no length limit.

Just remember to pull a ground.

~matt
 

e57

Senior Member
Is there a maximum run for flex conduit in indoor applications?

I've never used the stuff before and I never noticed any tables in my reference books, but there's got to be a limit right?.
Put a pull string in it before you enclose or conceal it. It aint great to fish through anyway when its long - even more so when you cant get a fish in it in the first place.... The slightest sag will add friction, add a few and you're finished in a long run.
 

480sparky

Senior Member
Location
Iowegia
Length of run is limited only by your ability to pull conductors through. If you buy 2500' spools of wire, you can install 2499' of FMC.
 