The NEC says that for an instantaneous CB used as part of a listed combination starter, the adjustable setting on the CB may be a maximum of 8x the motors FLC, or if proven by engineering review up to 17x the motor FLC. My question is why are these maximums chosen, and what advantage is there for setting the breaker as low as possible? Obviously it would allow better protection, but what are you risking or giving up by dialing the breaker to higher values?
One example I have been discussing recently involved a motor with a .75A FLC. Someone wanted to use a 7A breaker and I explained to them that this was too big and was a code violation because even the lowest setting on the 7A breaker is (3x rating) 21A which is much greater than the absolute max of 17x FLC allowed for the motor. It is even much greater than the 8x FLC you should start with.
I am saying that this motor needs a 1A breaker (if made in that size) this way the breaker is adjustable from 3A to 10A and is within the allowable range. The more I think about it though I'm thinking that maybe a 3A breaker should be used to allow higher adjustments if necessary however even the lowest setting of 9A would be greater than the 8x your supposed to start with. I'm not sure of the typical increments of breaker sizes for this type of MCP breaker so I wanted to hear other opinions.
One example I have been discussing recently involved a motor with a .75A FLC. Someone wanted to use a 7A breaker and I explained to them that this was too big and was a code violation because even the lowest setting on the 7A breaker is (3x rating) 21A which is much greater than the absolute max of 17x FLC allowed for the motor. It is even much greater than the 8x FLC you should start with.
I am saying that this motor needs a 1A breaker (if made in that size) this way the breaker is adjustable from 3A to 10A and is within the allowable range. The more I think about it though I'm thinking that maybe a 3A breaker should be used to allow higher adjustments if necessary however even the lowest setting of 9A would be greater than the 8x your supposed to start with. I'm not sure of the typical increments of breaker sizes for this type of MCP breaker so I wanted to hear other opinions.