Re: Maximum Size Breaker for #12 Branch
Originally posted by RUWired:
Tryinghard, If this 14 amp fla is including all loads on the equipment;the min circuit amps would be 14x125%=17.5.If this unit has t.o.l protection ;then max brkr would be 14x175%=24.5(25)amp breaker.A disconnect is required at the unit.If the unit requires fuse/hacr protection,then installing a hacr brkr in the panel serving the branch ciruit is good with out the need of fuses.if not then a fused disconnect at the unit is needed.
Rick
Okay; the 25A breaker in a remote panelboard is existing and the replaced unit was circuited with #12?s so it must have had T.O.L.?s.
Now the new unit draws 14 FLA x 125% = 17.5A and (with info I have received from Mech. does not require T.O.L.).
The basic rule is #12?s = 20A & #10?s = 30A? but there are exceptions to this basic rule and they are revealed in 240-4(G).
From what I understand from this string of information most, if not all, agree this application qualifies #12?s on the 25A breaker because it is HVAC equipment and 440 parts III, VI,
except for me!
Let me attemp to pick up what you may be referancing in NEC, if 440-22(A) does not apply because I do not have T.O.L.?s I then continue on to 440-52(3) & (B)(3) which qualifies the 125% of FLA. If this is not the exception you are referencing I am certainly lost and am curious; what/where in 440 III, VI qualifies the exception to allow #12?s on 25A breaker in my application? If you are correct in your reply to me earlier then the existing 25A breaker needs to be changed to a 20A and the local fused disconnect is redundant. If I am wrong in this thinking how so?
Now back to my scope I have #10's from the existing 25A breaker to a local fused disconnect at the new unit, which will most likely have 20A fuses for the new unit. Again with info I have received from Mech., the author of this change, I can see nothing wrong with my scope.