brantdavid
Member
What is the maximum size breaker that the NEC allows to feed heat trace cable that is constructed with #14 awg buss wire?
I would like to use a 30 amp 2 pole EPD breaker with #10 awg wire connected to the heat trace cables. I have 3 runs of heat trace cable - 100ft, 30ft & 25ft. Voltage is 208V. The cable will be on the roof of a building.
I would normally protect the wiring in accordance with it's ampacity.
Thank You.
Dave Brant
I would like to use a 30 amp 2 pole EPD breaker with #10 awg wire connected to the heat trace cables. I have 3 runs of heat trace cable - 100ft, 30ft & 25ft. Voltage is 208V. The cable will be on the roof of a building.
I would normally protect the wiring in accordance with it's ampacity.
Thank You.
Dave Brant