090223-2018 EST
joeyww12000:
Prompted by your starting this thread I decided to make some resistance measurements.
What Larry and others have said basically answered your question.
On to my experiments.
The goal was to measure both 60 Hz and DC resistance of a number 12 stranded copper wire and a 1/2 EMT conduit. DC resistance of copper wire is something readily available on the Internet. That or other sources serve as a reference.
In particular Belden lists the resistance of #12 stranded copper wire as 1.77 ohms per 1000 ft.
My experimental setup consisted of 4 terminal resistors. This is where voltage test points are separate from the current injection points and inboard of the current injection points. Look at how DC shunts are made. They work on AC as well.
On the #12 wire the voltage points were spaced 121" apart, 10.08 ft. On the conduit the spacing was 114", 9.5 ft. Insulators were made so the wire could be inside the conduit for some tests.
Resistance measurements were made at about 5 A for both AC and DC. Low voltage sources were used and a Powerstat was used to adjust input voltage to adjust output current.
The conduit was new and came from Home Depot. Its OD is 0.707" and ID is 0.620" for a wall thickness of about 0.043". The calculated cross sectional area is 0.6635*Pi*0.043 = 0.090 sq-in. The wire area is 0.00513 sq-in for solid. This is a ratio of 17.5 to 1.
My DC measurement of the wire produced 1.63 ohms/1000 ft. In the ball park of Belden's value. Multiple measurements on different days produced the same result. The AC measurement was within 1.5%, but lower. The experiment needs further refinement to be sure this is a valid difference.
DC conduit measurement produced 0.70 ohms/1000 ft.
Over a 10 length this corresponds to about 35 MV drop at 5A for the conduit, and about 81 MV for the #12 wire.
How does this relate to your problem. Suppose there is a conduit running between the main panel and the sub-panel, there is an EGC also between the two, and the neutral is connected to both main and subpanel enclosures. Any neutral current will be divided between the neutral, the EGC, and the conduit. Maybe half or more is thru the conduit.
A separate EGC and the conduit are expected to be in parallel. If the application includes conduit then lightly clean a spot on the conduit close to the main panel, and one close to the subpanel. Use a millivolt capable meter to measure the voltage between the two points. Activate the loads that produce the maximum neutral current. If there is no bonding of neutral to EGC in the subpanel, then the voltage across the conduit should be virtually zero. You must make good electrical contact at the voltage test points.
If you suspect stray magnetic fields are producing part of the reading, then remove the meter leads from the test points and connect a wire between the two meter leads but keep the geometry approximately the same. If the reading is approximately 0, then stray fields are insignificant.
Larger conduit will require greater current for the voltage readings I described.
.