Keep in mind that the same thing happens one the neutral. We just don't want what should be grounded surfaces to be likewise enrgized.Basically because of resistance, there is a potential difference from one end to the other in the EMT, or any conductor for that matter, so if there is imposed current from paralleling neutral current by bonding at both the service disconnect and a subpanel you could read voltage between two points on the conduit at the subpanel and back to the MDP when you had a length long enough to create enough a potential difference because of resistance?