hello,
first time poster here. Always browsed around here and i have a question.
i currently have a new 1000A 3PH 120/208 service and it is designed as the following
1) 1000A Fusible Disconnect
2) 1000A Bussed Gutter
3) 9x meter enclosures
4) 9x 100a fusible disconnects
This is my first build in this particular situation, i have always worked around with CT meters with services this size.
When regarding my MBJ, it should connect to my grounded conductor at my 1000A disconnect, however, the feedthrough meter enclosures have the grounded conductor lugs bolted directly to the enclosure, which in theory would allow current to travel through the meter enclosure, gutter enclosure, and interconnecting conduits between. Is this correct? I feel like the only way to break that bond at the meter enclosure would be to use PVC from meter enclosure to bussed gutter.
Am i missing something here, or is this normal? Maybe i am over-thinking it Meter enclosures provided by local power company
Also, in regards to bonding locations, technically are unmetered bussed gutters considered accessible? I had always thought that all bonding needed to remain accessible, similar to how bonding bushings are not allowing in the meter enclosure, because it is technically locked out by the power company
Any thoughts, insight, wealth of knowledge would be greatly appreciated
Thanks!
first time poster here. Always browsed around here and i have a question.
i currently have a new 1000A 3PH 120/208 service and it is designed as the following
1) 1000A Fusible Disconnect
2) 1000A Bussed Gutter
3) 9x meter enclosures
4) 9x 100a fusible disconnects
This is my first build in this particular situation, i have always worked around with CT meters with services this size.
When regarding my MBJ, it should connect to my grounded conductor at my 1000A disconnect, however, the feedthrough meter enclosures have the grounded conductor lugs bolted directly to the enclosure, which in theory would allow current to travel through the meter enclosure, gutter enclosure, and interconnecting conduits between. Is this correct? I feel like the only way to break that bond at the meter enclosure would be to use PVC from meter enclosure to bussed gutter.
Am i missing something here, or is this normal? Maybe i am over-thinking it Meter enclosures provided by local power company
Also, in regards to bonding locations, technically are unmetered bussed gutters considered accessible? I had always thought that all bonding needed to remain accessible, similar to how bonding bushings are not allowing in the meter enclosure, because it is technically locked out by the power company
Any thoughts, insight, wealth of knowledge would be greatly appreciated