Unique installation at radio tower sites. Radio tower sites use Emergency Generators with an ATS. Some are configured as SDS, and most are NOT SDS. Typically the AC service drop is at the Meter Can, and Disconnect is located on the outside wall of the equipment shelter building. Service enters into a hybrid service rated Main Distribution Panel with built-in ATS and TVSS. Located above or adjacent to the service entrance is the Hatch Entry Plate, where all coaxes and other services enter the building. All to create a true Single Point ground where everything entering and leaving the building can be properly bonded to a single point. The site uses a Ground Ring, Chem Rod, Tower Piers, Building steel, CCE, and Radials for the GES. The equipment shelter Ground Electrode Conductor drops straight down to GES. The N-G bond is at the ATS .
However, I have a few tower sites that do not fit that model out in cow pastures and mountain tops. The AC Power is delivered outside the fenced compound on a Utility Pole. The Meter Can and Service Disconnect are located on the utility pole, and they are using the Pole-Butt ground as the GES, which is NOT bonded to the site GES. The pole is 100 cable feet away from the building being served. There is a 4 conductor feeder (Li. L2, N, and G) going to the Equipment Shelter ATS from the utility pole.
I need to treat the Feeder as a Service to bond the Neutral again to create a single Point Ground. Here is the big issue. Tower sites use 48 volt DC power. The 48-volt plants are referenced differently from the AC Equipment ground 100 feet outside the compound. Towers are struck by lightning with about every passing storm. The AC Ground and DC ground come in close proximity inside the rectifiers. The DC Plant is Separately Derived. During a lightning fault, the DC and AC ground are at extreme voltage differences causing major damage.
So what loophole or exception does NEC provide me to do that? I need the N-G bond at the ATS, which is rated as service equipment. Essentially I have 2-Service Disconnects—one out on a pole and another at the ATS.
FWIW the radio tower is owned and operated by the same electric utility supplying electric power.
However, I have a few tower sites that do not fit that model out in cow pastures and mountain tops. The AC Power is delivered outside the fenced compound on a Utility Pole. The Meter Can and Service Disconnect are located on the utility pole, and they are using the Pole-Butt ground as the GES, which is NOT bonded to the site GES. The pole is 100 cable feet away from the building being served. There is a 4 conductor feeder (Li. L2, N, and G) going to the Equipment Shelter ATS from the utility pole.
I need to treat the Feeder as a Service to bond the Neutral again to create a single Point Ground. Here is the big issue. Tower sites use 48 volt DC power. The 48-volt plants are referenced differently from the AC Equipment ground 100 feet outside the compound. Towers are struck by lightning with about every passing storm. The AC Ground and DC ground come in close proximity inside the rectifiers. The DC Plant is Separately Derived. During a lightning fault, the DC and AC ground are at extreme voltage differences causing major damage.
So what loophole or exception does NEC provide me to do that? I need the N-G bond at the ATS, which is rated as service equipment. Essentially I have 2-Service Disconnects—one out on a pole and another at the ATS.
FWIW the radio tower is owned and operated by the same electric utility supplying electric power.