Is it required by code to use anti shorts on mc wire?
Is it required by code to use anti shorts on mc wire?
all the previous being said I use them religously all the time. It only takes one callback and a long troubleshoot to see how easy it would have been to install one of these little helpers.
No one posted NEMA 90?:huh:
that is really good information.
Is that valid when debating with the inspector or they want to see the cut sheet or instructions from the manufacturer.
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet66
all the way at the bottom of the 3rd page it says "antishort bushings are not required"
The key here is using listed for MC connectors.
That means no romex conn. or similar BX type, they must be rated for MC without a bush.