R Rzep34 Member Location Tx Occupation Inspection Apr 29, 2021 #1 Hello All, My contractor installed CGB’s on both ends of a 5kv 3c/1/0 MC cable is this legal? If not where can I find the answer in the code book? Thanks, RZ
Hello All, My contractor installed CGB’s on both ends of a 5kv 3c/1/0 MC cable is this legal? If not where can I find the answer in the code book? Thanks, RZ
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 29, 2021 #2 250.4(A)(3) requires the sheath be bonded, and 330.6 requires the use of fitting listed and identified for use with MC cable.
250.4(A)(3) requires the sheath be bonded, and 330.6 requires the use of fitting listed and identified for use with MC cable.
R Rzep34 Member Location Tx Occupation Inspection Apr 29, 2021 #3 don_resqcapt19 said: 250.4(A)(3) requires the sheath be bonded, and 330.6 requires the use of fitting listed and identified for use with MC cable. Click to expand... Thank you sir
don_resqcapt19 said: 250.4(A)(3) requires the sheath be bonded, and 330.6 requires the use of fitting listed and identified for use with MC cable. Click to expand... Thank you sir