Exception No. 5 to 310.15(B)(2)(a) is ALL inclusive.NYC Elect said:Rule 310.15 Exemption (5) (2) also says that if the conductors are 12 awg copper this rule does not apply...So in my case, if I have 12/3 MC, do I even have to worry about the derating factor?
The rule APPLIES to #12 [ item (2)]Exception No. 5:
Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(1) Each cable has not more than three current-carrying conductors.
(2) The conductors are 12 AWG copper.
(3) Not more than 20 current-carrying conductors are bundled, stacked, or supported on “bridle rings.”
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
Joe Villani said:With 15 12/3 mc cables I am calculating at least 30 current carrying conductors so exception #5 (3) woulld not apply.
infinity said:How did you come up with 30 CCC's?
emahler said:I would like to know how to get 3 circuit and a neutral from 12/3 MC.
infinity said:I would assume that these are three wire circuits with a neutral that is a CCC from a 208Y/120 volt system. That gives you 45 CCC's.
infinity said:I'm assuming that there are 2 circuits with one neutral in each three wire cable. When fed form a 208Y/120 volt system all three conductors count as CCC's.