WeisD
Member
- Location
- Colorado Springs, Colorado
Question: There are eight 10-3 MC cables grouped together without spacing run through a plenum space above a hard lid ceiling. The cables are exposed to an area where temperatures of 155° F are often encountered. The circuits are fed from a 120/208, 3 phase, 4 wire panel. What is the corrected ampacity of the conductors within the MC cables? 60% of 40 Amps per 310.15(B)(3)(4) exception to (4):, or, multiplier of .58 from 310.15(B)(2)(a)?